The Above Grade Service Technical Community of Interest is a group of people (both AMPP members and nonmembers) who have come together for the purpose of furthering a common cause by sharing wisdom, knowledge, information, and/or data for pipelines and tanks that are utilized in above ground environments.
  • 1.  Degree of required cleanliness for touchup paint application on Hot-dipped Galvanized Structure

    Posted 02-14-2023 08:13 AM

    Dear Experts;

    The subject of query is related to "surface cleanliness on small damages prior to touchup paint application" on base plate of hot dipped galvanized structural members which were fully coated with surface tolerant epoxy mastic paint. 

    Paint damages found at base plate of several structural columns, the damages occurred due to washer plates (06nos.) welded on a base plate of hot dipped galvanized column, the reason galvanization layer is fully removed and substrate is visible from base plate, damages are adjacent to weld beads of washer plates including the extended heat-affected zone (HAZ) area which is approximately 25mm at all around the weld beads, See the below image PIC-2 for reference. The affected area is calculated by considering the maximum length and width of damage at base plate of a column which is less than 0.1m², See below calculation. 

    CALCULATION: (By choosing maximum length and width of damage)

    Area affected due to welding in surrounding of one bolt is 130*30*4 sides= 15600 mm²,                                                                                                                Area affected due to welding in surrounding of six bolts is 15600*6nos.=93600mm²=0.093m²,                                                                                                      Affected area is 0.093m² which is less than 0.1m².

     PREPARED THE SURFACE AROUND WASHER PLATES AT ONE COLUMN: The surfaces were prepared according to project requirements by using combination of tools represented in SSPC-SP2-hand tool and SSPC-SP3-Power tool, rusts and other contamination were fully removed as shown in PIC-1 that may detrimental to a coating system. Our company is proposing to give assurance of life span of applied coating by carrying out Peel-off adhesion test over cured coating with reference to ASTM D3359 type 'A'.

    But our client is not accepting the proposed methodology of surface cleanliness for applying touchup paint application by recommended paint that is surface tolerant epoxy mastic coating.

    In other hand, client is asking to check anchor profile on substrates those prepared in accordance to SSPC-SP2 & SP3 which is not included in our best practice. NEED EXPERT SUGGESTION.

    Are these surface preparation methods (SP2/SP3) are acceptable for small damages on hot dipped galvanized surface or need sweep blast.?



    ------------------------------
    Adeel Ahmad
    M/s. Tecnicas Reunidas Saudia
    Jazan Refinery and Terminal Project
    Kingdom of Saudi Arabia,
    Phone# +966554863154
    ------------------------------


  • 2.  RE: Degree of required cleanliness for touchup paint application on Hot-dipped Galvanized Structure

    Posted 02-15-2023 08:53 AM

    Dear Colleagues,

    Based on my experience , below is my opinion.

    01. Damaged areas to bare metal, abrasive blast(spot blast) to SA 2.5 

    02. If possible adhere to original system of galvanizing

    03. If not possible, apply Zinc Rich Epoxy (minimum of 80% zinc content) to 75-100µ DFT

    04. Multiple coats may require to achieve this DFT

    05. Continue with specified system.

    Positively it will be approved by client.



    ------------------------------
    George Kutty Yohannan
    S. India
    +91 9946827188
    ------------------------------



  • 3.  RE: Degree of required cleanliness for touchup paint application on Hot-dipped Galvanized Structure

    Posted 02-26-2023 10:43 PM
    Edited by Adeel Ahmad 02-26-2023 10:45 PM

    Thanks but I don't think to perform abrasive blast is a best practice for small damages on dipped galvanized base plate.



    ------------------------------
    Adeel Ahmad,
    Coating supervisor QA-QC,
    adeelahmad0000@yahoo.com,
    Saudi Arabia, +966554863154.
    ------------------------------



  • 4.  RE: Degree of required cleanliness for touchup paint application on Hot-dipped Galvanized Structure

    Posted 02-27-2023 08:07 AM

    Dear All,

    Actually there is no need for abrasive blasting for such small spot damages.

    I prefer the same because , the client was not accepting the recommended

    procedure.



    ------------------------------
    George Kutty Yohannan
    +91 9946827188
    george3342hotmail.com
    george3340@gmail.com
    ------------------------------



  • 5.  RE: Degree of required cleanliness for touchup paint application on Hot-dipped Galvanized Structure

    Posted 02-28-2023 09:07 PM

    Yes, Exactly Mr. George



    ------------------------------
    Adeel Ahmad,
    Coating supervisor QA-QC,
    adeelahmad0000@yahoo.com,