The Below Grade Service Technical Community of Interest is a group of people (both AMPP members and nonmembers) who have come together for the purpose of furthering a common cause by sharing wisdom, knowledge, information, and/or data for pipelines and tanks that are utilized in buried service environments.
  • 1.  High Voltage Holiday testing on pipes with CP systems

    Posted 11 days ago

    Hi all,

    I am having trouble finding any documentation pertaining to performing High Voltage Holiday Testing on underground piping that has a Cathodic Protection 

    system installed. Stopaq is being applied to the piping and 15kV is being used. Will it damage the the CP system?

    Cheers!



    ------------------------------
    James Foucault
    South River
    +17097275428
    ------------------------------


  • 2.  RE: High Voltage Holiday testing on pipes with CP systems

    Posted 10 days ago

    James,

    The holiday detection won't harm the CP system.  Even though the voltage is high, the amperage being pushed into the pipe by the holiday detector is low.  Also, the small current being put onto the pipe with the holiday detector is jumping off the pipe somewhere else to come back to the earth through your ground (or if you're grounded to the pipe, right back through the pipe to the detector).  The current isn't being sent back up the CP system to the rectifier.

    Many, many decades of holiday detection on pipes with impressed current CP systems running with no problems is the proof.  For documentation, maybe the holiday detector manufacturer has some literature about the amperage.

    Per Allied Construction's page on the Tinker/Rasor M1 holiday detector:

    "The detector operates from 110/120 volt 50/60 cycle A.C. line current. The electrical design of the M1/AC Holiday Detector utilizes a sensitive relay which is activated by a voltage regulated, solid state power supply. When a current of approximately 750 micro-amperes flows through the system the relay closes and actuates the signal bell."*

    *https://www.alliedcorrosion.com/product/holiday-detector-model-m1-ac/ 



    ------------------------------
    Neil Pittman
    Lake Superior Consulting
    Livonia MI
    +13137213301
    ------------------------------



  • 3.  RE: High Voltage Holiday testing on pipes with CP systems

    Posted 9 days ago

    Hi Neil,

    Thank you for the response, I really appreciate it!

    I have contacted the manufacturer and am just waiting on a reply.

    I had assumed that this scenario was common place but CP systems is an area that I have not been really involved with.

    Cheers!



    ------------------------------
    James Foucault
    South River